Megger questions

Location
Wyoming
Occupation
Electrician
I recently had to use a megger to test potentionally bad underground cables that power parking lot lights. On phase a I got an immediate 4000 meg ohm reading which is the highest the megger could read, and on phase b I got roughly 600 meg ohms. The circuit keeps tripping and it does not appear to be and of the wiring inside of the light. Am I reading the megger wrong? I had someone tell me that 1 meg ohm per 1kv of operating voltsge was acceptable, so according to him, 600 meg ohms should be more than enough. I guess I really don't understand the instrument itself and any help would be appreciated.

Sent from my SM-A037U using Tapatalk
 

ammklq143

Senior Member
Location
Iowa
Occupation
Electrician
If you haven't done so, make sure you isolate the conductors so you're only testing the them and not getting anything from the lights that interfere with the test. Also, disconnect the light and see if the breaker still trips when power is applied.
 

hillbilly1

Senior Member
Location
North Georgia mountains
Occupation
Owner/electrical contractor
Probably a bad ballast or driver if the circuits check good. Do not meg the fixtures unless you want to replace them. A simple ohmmeter test can usually find a bad ballast, a little harder for a driver. There should be zero continuity between the fixture wires and ground with the fixture disconnected. Another test is to clamp your ammeter around both fixture wires at the bottom of the pole with them on. You should get zero amps, if not, the fixture has a fault to ground.
 

Little Bill

Moderator
Staff member
Location
Tennessee NEC:2017
Occupation
Semi-Retired Electrician
Probably a bad ballast or driver if the circuits check good. Do not meg the fixtures unless you want to replace them. A simple ohmmeter test can usually find a bad ballast, a little harder for a driver. There should be zero continuity between the fixture wires and ground with the fixture disconnected. Another test is to clamp your ammeter around both fixture wires at the bottom of the pole with them on. You should get zero amps, if not, the fixture has a fault to ground.
What good would clamping the wires do if the breaker is tripped? OP said his breaker tripped.
 
Top