powerpete69
- Northeast, Ohio
- Professional Electrical Engineer
At what resistance level should 5 KV shielded cables be replaced when meggering?
I've read some things that say if you get below 1500 mega-ohms on any phase, replace cable.
I've read other things they say you can push it to 100 mega-ohms?
I've also read you need 1 mega ohm per thousand volts. So in this case, 5 Mega Ohms should be okay.
Personally, I've seen cable short circuit at 800 Mega ohms.
My actual cable in question has the following megger measurements from phase to ground:
Phase A: 1.8 Giga ohms
Phase B: 40 Mega-ohms
Phase C: 90 Mega-ohms
To me, this is a replace cable ASAP situation.
Also, they do VLF/Tan delta tests as well which requires 7,000 volts compared to 1,000 volts for megger test.
My electrician skipped the VLF/Tan delta test because he said we would likely blow up a cable with less than 100 mega-ohms on it if you put 7,000 volts across it.
Anyways, does anyone have any solid info on this from their experience?