powerpete69
Senior Member
- Location
- Northeast, Ohio
- Occupation
- Professional Electrical Engineer
At what resistance level should 5 KV shielded cables be replaced when meggering?
I've read some things that say if you get below 1500 mega-ohms on any phase, replace cable.
I've read other things they say you can push it to 100 mega-ohms?
I've also read you need 1 mega ohm per thousand volts. So in this case, 5 Mega Ohms should be okay.
Personally, I've seen cable short circuit at 800 Mega ohms.
My actual cable in question has the following megger measurements from phase to ground:
Phase A: 1.8 Giga ohms
Phase B: 40 Mega-ohms
Phase C: 90 Mega-ohms
To me, this is a replace cable ASAP situation.
Also, they do VLF/Tan delta tests as well which requires 7,000 volts compared to 1,000 volts for megger test.
My electrician skipped the VLF/Tan delta test because he said we would likely blow up a cable with less than 100 mega-ohms on it if you put 7,000 volts across it.
Anyways, does anyone have any solid info on this from their experience?
I've read some things that say if you get below 1500 mega-ohms on any phase, replace cable.
I've read other things they say you can push it to 100 mega-ohms?
I've also read you need 1 mega ohm per thousand volts. So in this case, 5 Mega Ohms should be okay.
Personally, I've seen cable short circuit at 800 Mega ohms.
My actual cable in question has the following megger measurements from phase to ground:
Phase A: 1.8 Giga ohms
Phase B: 40 Mega-ohms
Phase C: 90 Mega-ohms
To me, this is a replace cable ASAP situation.
Also, they do VLF/Tan delta tests as well which requires 7,000 volts compared to 1,000 volts for megger test.
My electrician skipped the VLF/Tan delta test because he said we would likely blow up a cable with less than 100 mega-ohms on it if you put 7,000 volts across it.
Anyways, does anyone have any solid info on this from their experience?