SmithBuilt said:What voltage are you testing at.
For 208 volts?
For 480 volts?
And do you use the same criteria for both voltages? I see Brian stated his 480 volt cirteria. What would it be for 208 volt system or would it be the same since the wire is rated for 600v?
It dosent matter what the operating voltage is, what matterrs is the voltage rating. 600V rated insulation should be tested at 1000V or more, lower voltage ratings tested at 500V.