Megger

Status
Not open for further replies.

brian john

Senior Member
Location
Leesburg, VA
I put this together this afternoon and have some pics to add, I really was not sure were to post. This is a first draft and I welcome corrections, additions questions.

Questions often arise regarding the use of Meggers I have posted some information, that hopefully is useful. Some of the information noted below is based upon personal experience; all users should familiarize themselves with the correct test criteria and test equipment prior to performing any work. Testing is NEVER completed on energized equipment. If you are not sure about your results HIRE a company that has experience in the test you are performing or obtain help in determining the results prior to possibly damaging yourself or the distribution system you are working on. Lastly NEVER rely on a continuity tester or ohm meter to check any distribution system for shorts/faults. This is a good way to damage the distribution equipment, hurt yourself or worse and of course you could end up on the wrong end of a lawsuit.
-------------------------------------------------------------------------------------------------------------------------------------
From Wikipedia:
A megger (or sometimes meggar) is often used as an alternate term for an insulation tester - a circuit tester which puts a very high voltage at a very low current across two conductors to make sure that they are properly insulated. The word is short for megohm-meter.
It is in fact the registered trade mark of Megger Group Ltd who have manufactured insulation testers since 1889.
Older types of insulation testers have a small built-in generator turned by the handle. Modern types work with batteries and circuitry to generate the voltage required.
-------------------------------------------------------------------------------------------------------------------------------------
Megohm = 1,000,000 = one million ohms
Gigohm = 1,000,000,000 = one billion ohms
Terohm = 1,000,000,000,000 = one trillion ohms
-------------------------------------------------------------------------------------------------------------------------------------
Today meggers typically come is 3 basic styles.
1. Analog and can be line voltage, battery, hand crank or a combination of two
2. Digital and can be line voltage or battery operated or both.
3. Digital with an ?analog? scale these are also line voltage or battery operated or both.
Typical DC voltages available are 50. 100, 250, 500, 1,000, 2,500, 5,000 and 10,000 or some combination of these.
A decent megger for the ?average electrician? has 250, 500 and 1,000 DC voltage settings, though I really like a megger that has a 50 or 100 VDC test voltage (in addition to 250, 500 and 1,000 VDC settings) as it allows me to pre-test a circuit with a certain sense of I am not going to fry something sensitive. I also prefer a digital analog style meter.
There are additional megger types for special test, but I have not included these as they are outside the scope of what the average electrician should have in his ?tool case?
See attached photos
-------------------------------------------------------------------------------------------------------------------------------------
Meggers can be utilized to test all distribution equipment with a few considerations.
1. Length of conductors will affect the readings and you need to take this into account that there is a time to charge the conductors (typical times are one minute).
2. Long conductor runs will ?hold a charge? always ground the conductors after testing.
3. Readings that fluctuate often indicate moisture and/or water. Leaving the megger connected can in some cases ?dry out the problem? Though if moisture or water is an issue obviously this warrants further investigation.
4. You have to be careful that all loads are disconnected, meters, relays; control transformers can skew readings and/or show as a fault. Nothing worse than telling a customer they have a dead short when in fact it is a tenant sub meter.
5. Meggers can be utilized on
Transformers - Primary to secondary, primary to ground and secondary to ground (assuming any grounded conductor has the connection to ground isolated).
Motors - line to ground (with transformers and motors phase to phase connections should read as a dead short) There are additional test used on motors and transformers this megger test mentioned here are basic go no go field test.
Circuit breakers disconnects, motor starters - with the load disconnected, pole to pole line, pole to pole load, line to load (CB open).
Feeders to include busway - Phase to phase, phase to neutral phase and phase and neutral to ground.
Switchboards, panel boards, MCC?s ECT - Phase to phase, phase to neutral phase and phase and neutral to ground.
Branch circuits ? Phase to Phase, phase to ground and the often overlooked, neutral/grounded conductor to ground.
-------------------------------------------------------------------------------------------------------------------------------------
There are test standards and specifications available for all megger test to be performed, these include NETA, NEMA.
http://www.netaworld.org/
http://www.nema.org/
?-------------------------------------------------------------------------------------------------------------------------------------

There are also some basic ?rules of thumb?, for go no go testing also commonly referred to as spot reading and generally the most common test most electricians will perform..
If the distribution equipment in question has gotten wet, experienced a fault that results in carbon deposits IT IS IMPERATIVE a company that specializes in this type of problem be contacted. In the way to many cases (one was too many) of injury and death I have been involved in, water and previous faults were the number one and number two causes of injury/death.
This test applies to conductors that are existing. Obviously we would like a full scale reading (infinity) which depending on the megger can be 1000 megohms, 2000 megohms, 4000 megohms or some meggers have higher megohm readings. One thing to remember about infinity FULL SCALE readings, Infinity on you meter can be beat by another meter this all depends on the full scale of the megger in use and the test voltage.
It is possible to damage equipment with a megger if you apply too high a test voltage, so it is imperative you know what you are testing and what is connected to what you are testing.
Typically I like to see high readings 50 megohms or higher, additionally if the readings phase to ground are A-phase 1000 megohms, B-phase 75 megohms, C-phase 1000 megohms, there may be something happening with the B-phase and while an acceptable reading this may warrant investigation.
I hesitate to say that there are cases where I have had reading below 50 megohms where the distribution equipment was re-energized with mitigating circumstances. BUT in all cases the readings were above 5 megohms and the customer was made aware of the situation and signed off on the re-energizing. A good example of this would be underground feeders and/or branch circuits.
?-------------------------------------------------------------------------------------------------------------------------------------
So you have a megger, you have read the instruction manual, you read AECM and Megger links below now you are ready to test something.
Set the megger to the lowest voltage scale and insert the test leads. Put you gloves on (rubber and leathers), hold the test leads apart and push the test button, the meter should go to full scale (air in most cases is a good insulator), that is an excellent reading. Next touch the leads together and push the test button this is a dead short the megger should read ?0?. Now get some paper and a no. 2 pencil and scribble lines two large patches for your test clamps and numerous interconnecting lines. Using different voltage settings hit the test button, the meter may give an infinity reading or some reading in between, or it paper and lines may arc and spark till the paper either catches fire or clears the ?FAULT?. With different paper thickness varying the scribbles and changing the test voltage you should be able to get an idea of your meggers reading.
Another test that for some reason always amazes some electricians is to connect your multimeter to the test leads (assuming you multimeter can handle the applied voltages) of the megger and push the test button to check the test voltage. Normally the megger output is a few volts above the published test voltage, i.e. 1000 VDC on the megger results in 1052 VDC on the multimeter.
?-------------------------------------------------------------------------------------------------------------------------------------
 
Last edited by a moderator:

brian john

Senior Member
Location
Leesburg, VA
FIRST POST WAS TOO LONG.......


What megger should you buy?

In my opinion there are 3 basic meggers I would consider

All should have variable testvoltages up to 1000 VDC, be digital with analog scale, 2000 megohms or more full scale readings. And just my experience buy a Fluke, AVO Biddle Megger, or AEMC brand. Additionally I would recommend calibration of you megger, multimerter and amp clamp at least every few years (we cal all our equipment yearly). Figure on spending between 300.00-700.00 dollars. Obviously the better meters with options to include multiple test voltages are going to cost you... Get a good case and hopefully treat it like you do your multimeter (which is like you life depends on it, because it does). At a minimum select an insulation resistance tester, with 250, 500, 1,000 VDC ranges a tester with 100 VDC would be included in any megger I purchase.
Fluke and AEMC do not mention the Trade name Megger [I think] they list these testers as insulation resistance testers Megohmmeters.
AEMC
http://www.aemc.com/techinfo/Charts/Megohmmeter/Megohmmeter_Comparison_Chart.pdf
Megger
http://www.biddlemegger.com/cgi-bin...nbeyemiw121002645030&command=link--bi2820.htm
Fluke
http://us.fluke.com/usen/products/categoryinsul.htm
-------------------------------------------------------------------------------------------------------------------------------------
The best way to familiarize yourself is to test everything and document your results (for many reasons) and test often. Play with the tester. If the results seem questionable, question yourself, your test procedures, check the megger, leads apart then leads shorted.
Additional reading:

AEMC
http://www.aemc.com/techinfo/techworkbooks/megohmmeters/tech_megohm.pdf

Megger
http://www.omnicontrols.com/articles/Megger-A_Stich_in_Time.pdf

Fluke
http://support.fluke.com/find-sales/Download/Asset/1579160_6115_ENG_C_W.PDF

Additional reading
http://www.hipot.com/faqs/insulation.shtml
http://ecmweb.com/mag/electric_testing_insulation_save/index.html
http://www.sefelec.com/en/insulation-resistance-test.php
http://bg.ecmweb.com/ar/electric_insulation_testing/index.htm

Search the web??.
 

charlie k.

Senior Member
Location
Baltimore, Md.
Megger

Good post Brian, the megger is required tool for commissioning and testing gear, equipment and systems. Even though we have all our gear, motors and large cables tested by an independant test co. I still like to check again before we energize. It is important to document your readings, it may come in handy down the road.

Charlie
 

zog

Senior Member
Location
Charlotte, NC
brian john said:
ICircuit breakers disconnects, motor starters - with the load disconnected, pole to pole line, pole to pole load, line to load (CB open).
---

Well done Brian, I was thinking we needed a good FAQ on this topic. I have to point out that on breakers/starters, it should be Phase to Phase (Breaker closed), Phase to Ground (Breaker closed) , line to load (Breaker open)

I have some good stuff on the 3 currents measured, I will post and you can add if you like.
 
L

Lxnxjxhx

Guest
". . .it is sooo much fun to set fires."

". . .it is sooo much fun to set fires."

Brian John, I would think you will soon be hearing from Charlie Eldridge.

"I know we are all electrical professionals; however, everyone who reads these posts is not necessarily an electrical professional. I would hope that no one would be stupid enough to actually follow your advice. Assume for a moment that there was enough impedance in the circuit to delay the overcurrent device for the circuit from opening; have you caused someone to start a fire? OK, assume the available fault current was high enough to do as you have suggested; has the practical joker been aware that maybe there shouldn't be anything around that would catch fire?

I know I am coming down with both feet but this is something for either an accident or a test bench, not to be done on purpose to someone with limited electrical knowledge.
__________________
Charlie Eldridge, Indianapolis, Utility Power Guy"
 

zog

Senior Member
Location
Charlotte, NC
Lxnxjxhx said:
Brian John, I would think you will soon be hearing from Charlie Eldridge.

"I know we are all electrical professionals; however, everyone who reads these posts is not necessarily an electrical professional. I would hope that no one would be stupid enough to actually follow your advice. Assume for a moment that there was enough impedance in the circuit to delay the overcurrent device for the circuit from opening; have you caused someone to start a fire? OK, assume the available fault current was high enough to do as you have suggested; has the practical joker been aware that maybe there shouldn't be anything around that would catch fire?

I know I am coming down with both feet but this is something for either an accident or a test bench, not to be done on purpose to someone with limited electrical knowledge.
__________________
Charlie Eldridge, Indianapolis, Utility Power Guy"

Huh? What are you talking about, he is talking about a test bench. And why are you using Charlies signature?
 

mivey

Senior Member
brian john said:
The paper test (about the 5th time posted here) but it is sooo much fun to set fires.

Double click on the image below.

That is a painfully slow scroll. I gave up waiting for the fire.
 

rexowner

Senior Member
Location
San Jose, CA
Occupation
Electrician
brian john said:
There are additional megger types for special test, but I have not included these as they are outside the scope of what the average electrician should have in his “tool case”

Brian,

I would also like to thank you for taking the time it
obviously took to put together this educational post.

I am a little confused on the relationship with another
form of testing, earth-ground testing. I have heard
a number of times, "you can test ground resistance
if you have a megger.", including on a post this evening
about ground rods.

E.g. ground and insulation testers are aimed at opposite
ends of the resistance scale, although I have yet to
ascertain what voltage earth ground resistance work at
which is leaving some unclarity in my mind.

I have read through manufacturer literature on ground
testing (pointed at from you in another post - thanks!).
It appears to me that while Megger (and AEMC, Fluke)
manufacturers both insulation testers and ground testers,
these functions are completely distinct. Is this correct?

Sorry if this is kind of a newbie question, but I wanted to
make sure I had this straight next time someone talked
about testing ground resistance with a "megger".

Thanks.
 

76nemo

Senior Member
Location
Ogdensburg, NY
rexowner said:
Brian,

I would also like to thank you for taking the time it
obviously took to put together this educational post.

I am a little confused on the relationship with another
form of testing, earth-ground testing. I have heard
a number of times, "you can test ground resistance
if you have a megger.", including on a post this evening
about ground rods.

E.g. ground and insulation testers are aimed at opposite
ends of the resistance scale, although I have yet to
ascertain what voltage earth ground resistance work at
which is leaving some unclarity in my mind.

I have read through manufacturer literature on ground
testing (pointed at from you in another post - thanks!).
It appears to me that while Megger (and AEMC, Fluke)
manufacturers both insulation testers and ground testers,
these functions are completely distinct. Is this correct?

Sorry if this is kind of a newbie question, but I wanted to
make sure I had this straight next time someone talked
about testing ground resistance with a "megger".

Thanks.


Don't feel bad for asking that question Rex. Testing ground resistance with a megger:confused: I'd love to hear more on that. Never even heard that discussion before!!!!!!!!!!!
 

rexowner

Senior Member
Location
San Jose, CA
Occupation
Electrician
76nemo said:
Don't feel bad for asking that question Rex. Testing ground resistance with a megger:confused: I'd love to hear more on that. Never even heard that discussion before!!!!!!!!!!!

It's in the fifth message on this post tonight:
http://forums.mikeholt.com/showthread.php?t=99235
I don't mean to pick on anyone - the poster is probably
just referring to the Megger brand of earth ground testers,
and it's really more of a side point than a main point,
but since "megger" usually means an insulation tester,
I find it somewhat disorienting because I am only
currently learning about these testers.

I also heard it at an solar class about a year ago, but
that was before I understood anything about meggers
(which I basically learned from this forum and the
pointers to other materials posted) and to be honest I
didn't have a high degree of confidence in that instructor.
 
Last edited:

brian john

Senior Member
Location
Leesburg, VA
Digital analog megger 250 VDC-5,000 VDC with close up of meter.


Untitled-4.jpg


DSC_6384-1.jpg


Hand Crank/120 VAC line voltage analog megger.

MEGGER-1.jpg


DSC_6380-2-1.jpg


Battery/120 VAC line voltage Analog


MEGGER-2.jpg


Voltage selection on analog meters

MEGGER-3.jpg


Fluke Multimeter with Megohmmeter feature 500 VDC and 1000 VDC ranges.

FLUKE1.jpg


DSC_6386-1.jpg
 

zog

Senior Member
Location
Charlotte, NC
I have heard people say that too. I guess you could test earth resistance with t megger but you might as well pick a number out of a hat.

Megometers are designed to measure values in the millions and billion of ohms range, not 25, 5, or 1 ohm. Just like you could use an ohmeter to measure insulation resistane but it disent do much good, will probally just read O.L.

Plus all you could do at best is a 2 point test for ground resistance and we know thats pretty worthless.
 

brian john

Senior Member
Location
Leesburg, VA
Some techs and maybe even some manufactures (well only one) refer to a 2-point/3-point/4-point earth ground resistance tester and a earth ground megger. No sure why but this is a different animal. ZOG?

For a post like this the limited time of editing is a tedious PIA, I am sure there are good reaasons for the change but none that benefit me. AND IT IS ALL ABOUT ME.
 

zog

Senior Member
Location
Charlotte, NC
brian john said:
Some techs and maybe even some manufactures (well only one) refer to a 2-point/3-point/4-point earth ground resistance tester and a earth ground megger. No sure why but this is a different animal. ZOG?

Just a misconception of terms I would guess. You have a link to that manufacturer reference? I have a good guess who it will be.
 

zog

Senior Member
Location
Charlotte, NC
To add to Brians excellent OP, there are 3 currents being measured (Important to understand you are measuring current, no such thing as an ohmeter) this is very important to understand when testing inductive equipment.

(View attachment before reading on)

When a high DC voltage is first applied the total current (a) consists of three current components;

1. Leakage current
2. Capacitance charging current
3. Absorption current

Conduction/Leakage Current (b) - This current passes through the surface of the insulation. The magnitude of current flow depends on the resistance of the insulation. Surface leakage is usually not a problem because it can be eliminated through external cleaning.

Capacitive Current (c) - The insulating specimen appears, ideally, as a capacitor. As a DC voltage is applied to a capacitor initial charging current flows until the voltage drop across the component equals the source voltage. As the capacitor charges, its charging current decreases to a minimum. This is called its steady-state value.
Dielectric Absorption Current (d) - This current also appears at the initial application of test voltage the same as capacitance current. This current is required to polarize the insulating medium. In other words it is energy absorbed by the insulating system.
 