Depends on it the cable is de energized when you test it. If not you will get a really wild reading :grin::D

Depends on length of cable, voltage utilized to test, time duration of test, Read some, there is a wealth of knowledge on the WWW, just google, megger, AVO, AEMC and cable test.
 
500 volt test will not tell you much. You need a 5kv test to determine if the cable is bad. If the cable was new I would use about 10 kv.
 
500 volt test will not tell you much. You need a 5kv test to determine if the cable is bad. If the cable was new I would use about 10 kv.

Where did 500V come from? I agree it wont tell you much but I still dont see where he said that.

ANSI/NETA requires at least 2500VDC for a 5kV cable test. I wouldn't exceed 5kV though, not with DC being destructive, all the standards agree with that.

I would do a 2500VDC megger test followed by a VLF withsatand test, than once it is online do a PD survey to establish your baseline PD levels for future analysis.
 
Brian, I still think your in for a pretty "wild" reading if you attempt to megger a 5000 volt cable live. All the meggers I ever used all said not to test while energized, but then again I never tested any cables rated over 600 volts. Maybe , but I would bet not.
 
no title

no title

If you are testing to rule out dead short, then you should hope for a successful result in the Giga Ohm range. If, however, you are testing the insulation for weak spots, then another test is required that can yield mixed results. The test is commonly referred to as a "high pot" test and if the insulation is suspect you can expect a catastrophic failure at, at least, one of the afore mentioned weak spots.
 