WB82- I work in a power plant of a large utility company. Typically we megger motor just one phase of the motor to ground as the phases are all connected inside the motor. Most, if not all our motors only have 3 leads coming out of the connection box. The megger test is checking the condition of the ground wall insulation of the motor. We also check the phase to phase resistance reading and are looking for no more than a 10% difference max. If some of the windings are shorted or you have bad connections, then the resistance readings will be unacceptable. Sometimes you have to dis-connect the motor and eliminate the leads from the MCC to the motor. The only test that will find shorts between individual coils of wire in a phase is the surge test. At our plant, we consider a motor startable if it megs 1 megohm per each 1KV of running voltage plus 1KV. So, if you have 480 volt motor, we look for a minimum of 1.5 megohm or we won't start it. If a motor has to have heat applied to get the megger reading up, then it will need a rewind eventually as the insulation is either tracking to ground or absorbing moisture. On a good motor, a megger reading between phases will show a short. Another test we might do is called a Polarization Index test. It is like taking a 10 minute megger reading. You then divide the ten minute reading by the one minute reading to get a number between 1 and 10. Depending on what you get, it tells you the condition of your ground wall insulation. For a explanation of the PI test, see:
http://electromotores.com/PDF/InfoT?cnica/EASA/Using%20Polarization%20Index.pdf