I have no issues with a meg test from hot to ground or neutral to ground when a GFCI is in the circuit being tested.
Testing from hot to neutral however subjects not only the MOV installed between those two points but also the other electronics connected between those points to the test voltage. None of those elecronics or the MOV are connected to the EGC of the device so you have no path there unless you already have a failed component to start with, which is what the test is intended to find in the first place.
I might suggest only applying a 250 volt test signal to a piece of equipment with solid state components in it that is only designed to operate at a nominal 120 volts though. If you wish to test other portions of the circuit with a higher test voltage then maybe is a good idea to disconnect from the GFCI, before testing.
Testing from hot to neutral however subjects not only the MOV installed between those two points but also the other electronics connected between those points to the test voltage. None of those elecronics or the MOV are connected to the EGC of the device so you have no path there unless you already have a failed component to start with, which is what the test is intended to find in the first place.
I might suggest only applying a 250 volt test signal to a piece of equipment with solid state components in it that is only designed to operate at a nominal 120 volts though. If you wish to test other portions of the circuit with a higher test voltage then maybe is a good idea to disconnect from the GFCI, before testing.