I meg a 250 hp 480v motor used with a vfd and was wondering if my fluke 1578 is ok for the task. I got 2.2. gigs which is as high as the meter goes. I seem to get a lot of 2.2 readings and wanted to ask if I am megging right.
I disconnect the motor leads from the starter / or motor head and attach one to to the fluke lead and the other lead from the fluke to ground from the motor. The motor leads were 15' from the starter. A lot of the motors are 50, 85 ,100 hp motor / pumps that we meg.
I meg for a minute at a time on each of the three leads.
Thanks