yes, i understand that. what i am saying is that the EGC connected to the ground rod is terminated at the meter socket, the 100A breaker in the photo of the panel is the disconnect for this panel, the EGC from the ground rod should have been brought to this panel but was not. there is no disconnect between this panel and the meter socket. the nipple you see in the lower left corner is connected directly to the meter on the other side of the wall, but they knocked out the opening too big so the nipple isnt even touching the panel can.