That's classic "loose connection" causing high resistance and heat, resulting in the melted breaker.
No ground wire should be run from the meter. The grounding (EGC) begins at the service panel or first means of disconnect w/OCPD.
Incorrect. The EGC system should not start until the enclosure that contains the main disconnect, and should also be where the GECs terminate. Before that, there should only be the neutral, and everything that should be grounded, like the meter base, is grounded via the neutral.the EGC should have been ran with the feeders from the meter socket but there is only the 240 and neutral
Incorrect. The EGC system should not start until the enclosure that contains the main disconnect, and should also be where the GECs terminate. Before that, there should only be the neutral, and everything that should be grounded, like the meter base, is grounded via the neutral.
yes, i understand that. what i am saying is that the EGC connected to the ground rod is terminated at the meter socket, the 100A breaker in the photo of the panel is the disconnect for this panel, the EGC from the ground rod should have been brought to this panel but was not. there is no disconnect between this panel and the meter socket. the nipple you see in the lower left corner is connected directly to the meter on the other side of the wall, but they knocked out the opening too big so the nipple isnt even touching the panel can.
Is it just me or do I see some burn marks in a few places at the bottom of the cabinet?