jeff48356

Senior Member
In the past, I've failed a rough inspection due to the fact that I used plastic boxes in the vertical cold-air return spaces on some walls. I didn't know that I needed to use metal ones. But where is the Code reference stating that? I'm not sure if I've ever seen that written.
 
In the past, I've failed a rough inspection due to the fact that I used plastic boxes in the vertical cold-air return spaces on some walls. I didn't know that I needed to use metal ones. But where is the Code reference stating that? I'm not sure if I've ever seen that written.

300.22(C)(3)
 