Would this be a way of connecting MC into a plastic box? I've never given it much thought never mind done it. Just wondering if anyone has.What about using a bonding bushing with them?
Would this be a way of connecting MC into a plastic box? I've never given it much thought never mind done it. Just wondering if anyone has.
Yeah,The locknut connects it to the box. The bonding bushing is used to ground it.
I understand that.Just saying I haven't had a reason to have to do it.
It doesn't seem natural.
I answered basically this same question the other day. Guy wanted to run 6/3NM into a PVC box and wanted to use a plastic "push-in" connector. I didn't like it and said I would like to see a two-screw connector. But I had questioned whether it would have to be bonded. I suggested a bonding bushing.
Another guy want's to use a PVC box to house the contactors for an Ansul system. I asked how he was going to handle bonding the conduits and MC cables going into the box.
Doesn't seem natural to me either. You see PVC boxes on the shelves of all the big boxes. Never screw cover, hinged cover or rain tight metal boxes. So which ones do you think people are going to try and use?
-Hal
I see your point Larry, but isn't the whole purpose of a bonding busing to assure solid continuity when using a concentric knock out, to assure the grounded metallic pipe and its grounding conductor within maintain the same integrity.The metallic raceways can be bonded at the other ends of their runs, and EGCs can be added to maintain continuity if needed.
For GECs, yes, because of choke effects at lightning-induced currents and frequencies.I see your point Larry, but isn't the whole purpose of a bonding busing to assure solid continuity when using a concentric knock out, to assure the grounded metallic pipe and its grounding conductor within maintain the same integrity.
but with due respect .. were talking about ground bushings, besides when is an MC sheathing utilized as a grounding path , isn't it more so for protection and yes at the same time, tends to maintain grounding capabilities. The MC ground wire is truly the intended fault path. .. right ?And we're discussing plastic boxes here, not metallic
Funny, I just saw a This Old House segment where a homeowner wanted power at his shed. The electrician used two-screw clamps in plastic boxes to make the splices from THWN in underground PVC to Romex for the indoor sections. No bonding bushings anywhere. Looked quite "hack." It looked like he just went shopping at Home Depot for the segment.
SceneryDriver
OP was talking about NM cable and a metallic connector in a plastic box, you still need to bond that metallic fitting, grounding bushing would work great for that. Other option is to avoid using a metallic fitting. Nylon cable gland should work, larger ones can be a little pricey, but grounding bushing has a cost as well that at least offsets the difference some.but with due respect .. were talking about ground bushings, besides when is an MC sheathing utilized as a grounding path , isn't it more so for protection and yes at the same time, tends to maintain grounding capabilities. The MC ground wire is truly the intended fault path. .. right ?