I have two questions regarding metal wireways and conduit. First off some of the information for project.
1. Metal wireway is 4? X 4? duct
2. Conduit is 2-1/2? EMT
3. All wire is 12 AWG
4. All branch circuits are 20 amps
Question 1. In reading article 376-22 I know I can run up to 30 current-carrying conductors in the wireway (raceway) without derating. If I go over this at what percentage do I start derating conductors at? If I look at table 310.15(2)(B)(2)(a) do I start at 4-6 conductors (80%) or do I start at 31-40 conductors (40%)?
Question 2. The sub-contractor wants to install 2-1/2? conduit from the distribution panel to the 4? X 4? wireway. This is to gain access to the wireway (raceway) for all the branch circuits. Now I know that I can have up to 30 current-carrying conductors in the wireway but what about the conduit? Do I follow the guidance from Table 310.16 and derate in accordance with table 310.15(B)(2)(a)? Which would mean if I have 30 current-carrying conductors I would have to derate to 45% of the ampacity of 12 AWG
1. Metal wireway is 4? X 4? duct
2. Conduit is 2-1/2? EMT
3. All wire is 12 AWG
4. All branch circuits are 20 amps
Question 1. In reading article 376-22 I know I can run up to 30 current-carrying conductors in the wireway (raceway) without derating. If I go over this at what percentage do I start derating conductors at? If I look at table 310.15(2)(B)(2)(a) do I start at 4-6 conductors (80%) or do I start at 31-40 conductors (40%)?
Question 2. The sub-contractor wants to install 2-1/2? conduit from the distribution panel to the 4? X 4? wireway. This is to gain access to the wireway (raceway) for all the branch circuits. Now I know that I can have up to 30 current-carrying conductors in the wireway but what about the conduit? Do I follow the guidance from Table 310.16 and derate in accordance with table 310.15(B)(2)(a)? Which would mean if I have 30 current-carrying conductors I would have to derate to 45% of the ampacity of 12 AWG