I like that definition but what about a 12 x 12 wireway 12" long?a two dimensional plane made by imagining a cutting the wireway at a 90 degree angle
I like that definition but what about a 12 x 12 wireway 12" long?a two dimensional plane made by imagining a cutting the wireway at a 90 degree angle
Not sure I understand that exceptionAuxiliary gutters are rare. They only exist where they extend the space within another piece of equipment, and are typically an optional accessory supplied by the equipment manufacturer. If the item in question is connected to the other equipment via raceways, it is a wireway and not an auxiliary gutter.
If you have more than 30 current carrying conductors at a cross section, take a look at 310.15(A)(2) Exception in the 2017 code or 310.14(A)(2) Exception in the 2020.
Given that you've described it as having a distinguished axis (one of the dimensions is the 12" long dimension, the other two are the 12x12 dimensions), you still have a well defined axial direction. So the "cross" sections would still be the sections perpendicular to that axis.I like that definition but what about a 12 x 12 wireway 12" long?
And a proper cross section in the area of the yellow would have three wires in it.The area shown in A is not a cross-sectional area for any code purpose related to wireways.
Im sorry correction Would not have 3 wires in it.And a proper cross section in the area of the yellow would have three wires in it.
What part are you asking about?Not sure I understand that exception
When talking about conventional raceways (like EMT) presume you cut through the tube (with conductors inside) in same manner you typically cut them to get a desired length. However many conductors you cut through is the number of conductors at that particular cross section. Wireway is same thing but number of conductors has more chance of being different at different cross sections than for raceways because the accessible design of them.Can someone define the term cross section ?
yes, but number of conductors at any particular cross section can vary on a wireway because they can turn and exit along the length of the wireway. A raceway the number of conductors is going to be same at all cross sections unless a conductor simply ends in the raceway or leaves in a non code compliant manner.Wouldn't the cross sectional area in post #19 be by looking through the end cap of the gutter rather than into the front opening of it as it is depicted in the graphic?
JAP>
yes, but number of conductors at any particular cross section can vary on a wireway because they can turn and exit along the length of the wireway. A raceway the number of conductors is going to be same at all cross sections unless a conductor simply ends in the raceway or leaves in a non code compliant manner.
I like that definition but what about a 12 x 12 wireway 12" long?
Ok for agruments sake it's a 12" X 12" wireway 6" long?Given that you've described it as having a distinguished axis (one of the dimensions is the 12" long dimension, the other two are the 12x12 dimensions), you still have a well defined axial direction. So the "cross" sections would still be the sections perpendicular to that axis.
Cheers, Wayne
What is practical difference between that and a 12x12x6 junction box other than any name on the label?Ok for agruments sake it's a 12" X 12" wireway 6" long?