Meter bank jumper

Merry Christmas

The electron man

Senior Member
Location
Nyc
Occupation
Electrician
the company I work for has us jump all the meters on the meter-bank with #12 wire so we can test all the sub panels in the apartment and the branch circuits

The ocpd for eaxh apartment is 100A

How is using a #12 jumper safe ?
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
If there is little to no load nothing will happen to the jumper. If you're running high wattage electrcial appliances then there might be an issue.
 

Hv&Lv

Senior Member
Location
-
Occupation
Engineer/Technician
the company I work for has us jump all the meters on the meter-bank with #12 wire so we can test all the sub panels in the apartment and the branch circuits

The ocpd for eaxh apartment is 100A

How is using a #12 jumper safe ?
🤔
You're jumping across the meters?
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
You're effectively installing fusible links. My first boss tested transformers with #18 wire.
 