Meter bank jumper

The electron man

Senior Member
Location
Nyc
Occupation
Electrician
the company I work for has us jump all the meters on the meter-bank with #12 wire so we can test all the sub panels in the apartment and the branch circuits

The ocpd for eaxh apartment is 100A

How is using a #12 jumper safe ?
 
If there is little to no load nothing will happen to the jumper. If you're running high wattage electrcial appliances then there might be an issue.
 
the company I work for has us jump all the meters on the meter-bank with #12 wire so we can test all the sub panels in the apartment and the branch circuits

The ocpd for eaxh apartment is 100A

How is using a #12 jumper safe ?
🤔
You're jumping across the meters?
 
You're effectively installing fusible links. My first boss tested transformers with #18 wire.
 