110.26 only calls out working space for equipment likely to require examination, adjustment, servicing or maintenance. Meters/cash registers are not required in the NEC, so I would check with your POCO, or look in their customer service handbook
I know that graphic is showing working space but you just said NEC doesn't apply to meters from your previous post. The graphic says meters do have to apply to 110.26 but you said it doesn't so I'm a bit confusedThat graphic is showing working space, dedicated space is obviously different. Is it required? Most would say yes. Check with your POCO
I said meters are typically not required in the NECI know that graphic is showing working space but you just said NEC doesn't apply to meters from your previous post. The graphic says meters do have to apply to 110.26 but you said it doesn't so I'm a bit confused
If they are just meters, the rules in 110.26(E) do not apply. The dedicated equipment space rules only apply to "switchboards, switchgear, panelboards, and motor control centers".There is no doubt that meter banks shall follow working space clearances.
But does the dedicated space 6' clearance rule apply to meter banks? My guess is no but I want some reassurance.
What it’s specifically a Eaton meter bank with integrated circuit breakers?If they are just meters, the rules in 110.26(E) do not apply. The dedicated equipment space rules only apply to "switchboards, switchgear, panelboards, and motor control centers".
Those are very likely listed as panelboards and the dedicate space rules in 110.26(E) would apply.What it’s specifically a Eaton meter bank with integrated circuit breakers?
And many "meter banks" have switches/overcurrent devices in them, but if they don't they may not need NEC working space. POCO's still often have requirements though which may or may not include work space.If they are just meters, the rules in 110.26(E) do not apply. The dedicated equipment space rules only apply to "switchboards, switchgear, panelboards, and motor control centers".
How would I find out if they are listed as panels…Those are very likely listed as panelboards and the dedicate space rules in 110.26(E) would apply.
I care about dedicated space clearance, not working spaceAnd many "meter banks" have switches/overcurrent devices in them, but if they don't they may not need NEC working space. POCO's still often have requirements though which may or may not include work space.
Look in the catalog, or call mfg.How would I find out if they are listed as panels…
I’m not sure if this means eaton meter banks are not required to follow 6’ dedicated space clearanceTake a look at 110.26(A)(3) exception 2
also 230.66 where it says Meterbase s aren’t service equipment.
Combo panels are