Where does your N-G bond occur? If the bond occurs in the meter base, you must run L-L-N-G from the meter pan to the main panel. If the bond occurs in the main panel, you do not have to run the ground conductor; the meter base will be bonded to the neutral. Keep in mind that depending on the wiring method, the conduit may serve as the grounding conductor, so you may not have a green wire in the conduit even of the bond occurs in the meter base.
If the meter base contains overcurrent protection, you must separate the neutral and ground conductors; you now have a feeder and not service conductors.