Mike01 said:
the one-line only indicates 3 wires + ground from the landlord thru the meter into a disc then troff. spliced for the hvac unit and then to a 75kva xfmr. I just thought you had to have the neutral conductor for the meter to operate
Three points:
1) The space disconnect requires a grounded conductor, aka neutral, and this is where the service GEC's and premises EGC's all meet up.
2) Ahead of this point, the neutral and EGC are one and the same, so what you referred to as "+ ground" would be the grounded conductor.
3) As far as I know, most three-phase (and many single-phase) meters do have internal jumpers for a grounded conductor for the meter itself.