I am a Progress Energy North Carolina customer.
My billing rate is Residential Time of Use Demand rate.
My electric meter is a GE IRM 70-S.
The meter is both electronic and mechanical and uses a current transformer.
My electric service is 400 amps using 2, 200 amp panels mounted side by side on the opposite side of the wall from the exterior meter can/housing.
The meter's digital display continueously cycles displaying a register number and the value associated with that register.
Register 18 contains the value of 000.050, which according to the documents supplied by Progress Energy, is the "Watt Hour Constant". Customer service reps. have refered to this register as the Kh and also as the "meter constant".
My monthly bill indicates that a constant of 60 is used to calculate the actual KWH.
A meter technician from Progress Energy recently inspected my equipment and advised that the CT / Current Transformer had a ratio of 600:5.
The meter's digital display shows values for registers 1 - 23 except for registers 3,7,10,14,17, and 19.
My monthly bill indicates both the highest KW for on peak and off peak showing the KW, time, and date. Looking at several years of bill, the times shown are always on 15 minute boundaries either on the hour, 15 minutes past the hour, 30 minutes past the hour or 45 minutes past the hour.
Progress Energy Customer Service representatives are not trained to answer technical questions about their demand and time of use billing or measurement techniques and are reluctant to allow me to talk to more knowledgable individuals in the company, so I am posting my questions here seeking advice from members.
Given the above information:
1. What is the relationship to the value in register 18 "watt hour constant" which is currently 000.050 and the "meter constant" of 60 as indicated on my monthly bill?
2. What is the relevance of the CT ratio with respect to question 1 above?
3. What is the significance of the 15 minute interval with respect to demand billing, and does the meter record average demand over the 15 minute interval or peak demand.
4. PE customer service advised that the 15 minute interval was a moving window. If this is correct, why are all readings for the past 6 years on one of 4 times at fixed intervals?
5. PE indicates date and time for off peak KW on their bill, however none of the registers display the date and time for off peak. Where do they get this information?
6. Meter registers 22 and 23 indicate the date and time for the highest on peak KW for the current month. Does the time value indicate the beginning of the 15 minute interval or the end of the interval?
7. The definition for on peak times for Progress Energy changes twice a year. How does the meter programed with the correct times?
8. Are there registers that aren't displayed by the meter but are downloaded into the data collection device used by the meter reader each month?
Thanks in advance for your assistance and information.
My billing rate is Residential Time of Use Demand rate.
My electric meter is a GE IRM 70-S.
The meter is both electronic and mechanical and uses a current transformer.
My electric service is 400 amps using 2, 200 amp panels mounted side by side on the opposite side of the wall from the exterior meter can/housing.
The meter's digital display continueously cycles displaying a register number and the value associated with that register.
Register 18 contains the value of 000.050, which according to the documents supplied by Progress Energy, is the "Watt Hour Constant". Customer service reps. have refered to this register as the Kh and also as the "meter constant".
My monthly bill indicates that a constant of 60 is used to calculate the actual KWH.
A meter technician from Progress Energy recently inspected my equipment and advised that the CT / Current Transformer had a ratio of 600:5.
The meter's digital display shows values for registers 1 - 23 except for registers 3,7,10,14,17, and 19.
My monthly bill indicates both the highest KW for on peak and off peak showing the KW, time, and date. Looking at several years of bill, the times shown are always on 15 minute boundaries either on the hour, 15 minutes past the hour, 30 minutes past the hour or 45 minutes past the hour.
Progress Energy Customer Service representatives are not trained to answer technical questions about their demand and time of use billing or measurement techniques and are reluctant to allow me to talk to more knowledgable individuals in the company, so I am posting my questions here seeking advice from members.
Given the above information:
1. What is the relationship to the value in register 18 "watt hour constant" which is currently 000.050 and the "meter constant" of 60 as indicated on my monthly bill?
2. What is the relevance of the CT ratio with respect to question 1 above?
3. What is the significance of the 15 minute interval with respect to demand billing, and does the meter record average demand over the 15 minute interval or peak demand.
4. PE customer service advised that the 15 minute interval was a moving window. If this is correct, why are all readings for the past 6 years on one of 4 times at fixed intervals?
5. PE indicates date and time for off peak KW on their bill, however none of the registers display the date and time for off peak. Where do they get this information?
6. Meter registers 22 and 23 indicate the date and time for the highest on peak KW for the current month. Does the time value indicate the beginning of the 15 minute interval or the end of the interval?
7. The definition for on peak times for Progress Energy changes twice a year. How does the meter programed with the correct times?
8. Are there registers that aren't displayed by the meter but are downloaded into the data collection device used by the meter reader each month?
Thanks in advance for your assistance and information.