Meter Disconnect required.

Status
Not open for further replies.

Pvelectric

Member
Location
MA
Occupation
Electrician
Goodmorning All, In Mass. When we are required to upgrade a customer's service entrance riser on residential we have to change to a meter/main Disconnect, to replace old meter enclosure, ? Is if there is no need to change the existing panel in basement which is in good shape and has a main Breaker I do need to replace the existing 3 wire SE is deteriorated, can I just replace that with 3 wire SE if I am keeping the existing panel in tact. Or must i change out the cable to a 4 wire now that the 1st disconnect is with the Meter. And if I must change to a 4 wire now the existing panel becomes a sub panel I must seperate grounds and neutrals, but now my 3 wire existing electric range and dryer's do not comply possibly. Can I get some info on the code actual requirements with article references if anybody can help. Thanks
 
Status
Not open for further replies.
Top