Rickyboothe
Member
- Location
- Amarillo Tx
Our new inspector has requested that we remove the screw and strap on our 200 amp single phase 120/240 volt meter socket ( the middle terminal , the one with a tag that says do not remove except for a ungrounded service, which this is a standard residential service) and run our bonding conductor to the left hand ground lug and source side bonding bushing . I am confused . Why are we removing this strap when it says not to . We also have a bonding bushing on our service disconnect with the neutral and panel bonded together with a bonding bushing which I think is correct with our ufer terminated in it