Meter Location/Ground Rod
VIC1958
The electric meter is located on the utility pole which is probably 75' from the house. Over head service to house to service mast then into panel board. There is no grounding rod outside the house for the panel board, there is no grounding rod located at the meter. There is a grounding conductor running down the side of the pole into the ground servicing the coductors on the pole. Water service inside the house is also not grounded/bonded to the panel. Where should the grounding rod be located for this type of situation? This is in an older section of town and I beleive this is a isolated situation.
There should be 2 rods driven at the house near the main panel and the water lines should also be bonded to the panel. If they are metallic water lines underground for 10' or more then the connection to the water pipes needs to be within 5' of where the water lines enter the house.
So I am correct in assuming that the GEC running down the side of the utility pole in it self is not a sufficient ground for the meter housing or the panel board?
That is a utility ground rod. Usally in this area they have a short jumper from the meter spliced to the pole ground. If the POCO owns the meter loop & pole, the grounding is their problem and while you may make the suggestions, the POCO will be the one to make changes there. Bonding & GEs at the residence is the major concern.
2 rods at house is what is need today. If its not new then the fun begins. Services were not required to be grounded many years ago. So before you tag this job you need know date it was built and code year that was used. Likely it is grandfathered and no action can be taken.
Why would you ground the meter socket with a rod and gec? Your ground isn't established until your first overcurrent device. Until that point, the neutral is the ground and your meter pan is bonded with the internal bonding screw that holds the neutral lug down.
What’s weird here is the meter base on a utility pole? This a grounded type system though meaning the earth connection is established at the source (utility XFMR), after which all other buildings and structures shall have earth connection as well. Keep in mind the earth connections purpose is described in 250.4(A)(1) primarily lightning control, it is not the neutral current path that is the function of the "grounded conductor".
Notice 250.24(A)(1) the GEC connection can be made at any accessible point on the load end of the service drop to the neutral bonding location (service disconnect), this can take place at a meter base in between these points but usually this meter base is on the structure being served rather than a remote pole.
Some POCOs spec it that way.
We have many meters located at the pole. The customer still must ground and bond at the building which is where the disconnect is usually located and is usually the point of service.
Our AHJS don't allow a ground rod at a meter socket as the connection is not accessible after the meter is sealed.
Except if the POCO requires a ground rod