depending on your code cycleSo 3 wire from a remote POCO pedestal's OCPD to a dwelling unit is now allowed with the grounding and bonding done at the structure,
Correct?
Jap
depending on your code cycleSo 3 wire from a remote POCO pedestal's OCPD to a dwelling unit is now allowed with the grounding and bonding done at the structure,
Correct?
Jap
So 3 wire from a remote POCO pedestal's OCPD to a dwelling unit is now allowed with the grounding and bonding done at the structure,
Correct?
I have always preferred 3 wire to the house. Even ignoring the emergency disco stuff, I was always puzzled how most people seemed to want to put a service disconnect at a pedestal, even when its hundreds of feet from the pedestal to the house. I thin a lot of people are either irrationally uncomfortable running service conductors hundreds of feet, or just plain dont know the code and think they need a disco at the ped. IMO its less equipment, less connetions, less conductors, and a better fault clearing path since the neutral is almost always larger than an EGC would be.I'm battling the whole 3 wire 4 wire thing.
On a new service if there is a 200 amp breaker in the Poco pedestal remote from a dwelling unit we can call that the Emergency Disconnect and pull 3 wire from it to the structure and do all our grounding and bonding there?
Or
Us it still 4 wire from the pedestal and Neutral and Ground separate at the structure?
I have always preferred 3 wire to the house. Even ignoring the emergency disco stuff, I was always puzzled how most people seemed to want to put a service disconnect at a pedestal, even when its hundreds of feet from the pedestal to the house. I thin a lot of people are either irrationally uncomfortable running service conductors hundreds of feet, or just plain dont know the code and think they need a disco at the ped. IMO its less equipment, less connetions, less conductors, and a better fault clearing path since the neutral is almost always larger than an EGC would be.