Meter/main Combo to Load center grounds

Status
Not open for further replies.

ronsquandary

New member
Location
Ashland, Or, USA
I have a 200 A service to a meter socket which feeds a 200 A load center through a 2" nipple. There is no "main" breaker at either side (socket or load center). The load center doesn't have room for the number of circuits I need.

My proposed upgrade will give me two main breakers so that I can disconnect either the load center or both panels. The new meter/main has 8/16 spaces/circuits and will be located outside (surface mounted) as underground feed in 3" conduit. The new load center will be flush mounted inside.
I am changing out a 200 A meter socket to a 200 A Siemens meter/main (M/M) combo, w/ feed thru lugs, (feed thru lugs at bottom of Buss controlled by the 200 A main). I intend to wire from fd. thru lugs to a Sq D load center with its own 200 A main breaker. Does this make the load center a sub-panel or since it is wired in series with the meter/main is it just an extension of the meter main as regards bonding neutrals and grounds. The installation of these two new panels will be back to back with a 2" nipple with 3/0 Cu hots and 1/0 neutral. This M/M will have a #4 Cu solid or braided wire to two grnd. rods. No attachment to water pipes as service is in PVC. I do have an CEE (concrete encased electrode) currently attached to my existing load center though I am uncertain of its integrity. My existing load center has the grnd, neutral and enclosure bonded together and an additional #6 solid Cu wire to a questionable grnd. rod outside below the meter socket. The existing meter socket has no dedicated ground wire, and relies on the nipple/nut for bonding to the load center and its grounds.

My confusion is regarding the proper grnding of the load center.

The new Sq D (QO) load center has 4 bars attached by a screw to the neutral buss, but there is no screw attaching the neutral to the enclosure (there is provision for a bonding screw to attach to these neutral and ground bars to the enclosure though I don't have the screw). The label indicates that as service equipment I can attach grnd wires to unused openings in these bars, but it doesn't address whether to bond these busses to the enclosure). It seems I could remove two of these bars and attach them directly to the enclosure for grounding my circuits separate from the neutrals if that is the proper way to set this up (there are three locations in the enclosure with a single screw hole and two tits that would index with these bars presumably for attaching two of the four bars directly to the enclosure, and separate from he neutrals <or I could purchase two new grnd. bars and install there>.

Questions: For purposes of clarity; when I am talking of neutrals and neutral buss bars I am talking of attachment points for the white commons and bare ground wires for my circuits. NOT the 3/0 neutral attaching from the pole to the meter/main to the load center.

1) Treat new load center as a sub-panel, an I believe that would mean I need to either install new grnd. bars attached to the enclosure or steal two of the four grnd. bars from the neutral/grnd bar configuration that exists?

2) Treat the new load center as an (series) extension of the meter/main combo and find a bonding screw to bond the neutral, grnd. and enclosure?

3) Can I/should I, run a #4 bare Cu wire through the nipple from the meter/main into the load center and what do I do with it (a four wire set-up)?

4) If the load center needs the neutral/grnd busses attached to the enclosure where might I find such a bonding screw (it looks to be about 1/4 inch fine thread hole in the buss bar with the hole in the enclosure not threaded, like the screw would be self-tapping)? This would presume the load center is to be treated as an extension of the service entrance.

5) If the load center is to be treated as a sub-panel, am I correct that the ground bars need to be separate from the neutrals and attached to the enclosure?

6) When is it necessary to actually isolate the ground wires with an insulator?

7) Please provide any other questions and answers to other aspects of my proposed situation that I have missed.

Thank You for any/all input?
 
I am changing out a 200 A meter socket to a 200 A Siemens meter/main combo, w/ feed thru lugs, I intend to wire from fd. thru lugs to a Sq D load center with its own 200 A main breaker. Does this make the load center a sub-panel or since it is wired in series with the meter/main is it just an extension of the meter main as regards bonding neutrals and grounds....
Anything after the first disconect is a sub-panel and the neutrals and grounds are separate.
 
I have a 200 A service to a meter socket which feeds a 200 A load center through a 2" nipple. There is no "main" breaker at either side (socket or load center). The load center doesn't have room for the number of circuits I need.

My proposed upgrade will give me two main breakers so that I can disconnect either the load center or both panels. The new meter/main has 8/16 spaces/circuits and will be located outside (surface mounted) as underground feed in 3" conduit. The new load center will be flush mounted inside.
I am changing out a 200 A meter socket to a 200 A Siemens meter/main (M/M) combo, w/ feed thru lugs, (feed thru lugs at bottom of Buss controlled by the 200 A main). I intend to wire from fd. thru lugs to a Sq D load center with its own 200 A main breaker. Does this make the load center a sub-panel or since it is wired in series with the meter/main is it just an extension of the meter main as regards bonding neutrals and grounds. The installation of these two new panels will be back to back with a 2" nipple with 3/0 Cu hots and 1/0 neutral. This M/M will have a #4 Cu solid or braided wire to two grnd. rods. No attachment to water pipes as service is in PVC. I do have an CEE (concrete encased electrode) currently attached to my existing load center though I am uncertain of its integrity. My existing load center has the grnd, neutral and enclosure bonded together and an additional #6 solid Cu wire to a questionable grnd. rod outside below the meter socket. The existing meter socket has no dedicated ground wire, and relies on the nipple/nut for bonding to the load center and its grounds.

My confusion is regarding the proper grnding of the load center.

The new Sq D (QO) load center has 4 bars attached by a screw to the neutral buss, but there is no screw attaching the neutral to the enclosure (there is provision for a bonding screw to attach to these neutral and ground bars to the enclosure though I don't have the screw). The label indicates that as service equipment I can attach grnd wires to unused openings in these bars, but it doesn't address whether to bond these busses to the enclosure). It seems I could remove two of these bars and attach them directly to the enclosure for grounding my circuits separate from the neutrals if that is the proper way to set this up (there are three locations in the enclosure with a single screw hole and two tits that would index with these bars presumably for attaching two of the four bars directly to the enclosure, and separate from he neutrals <or I could purchase two new grnd. bars and install there>.

Questions: For purposes of clarity; when I am talking of neutrals and neutral buss bars I am talking of attachment points for the white commons and bare ground wires for my circuits. NOT the 3/0 neutral attaching from the pole to the meter/main to the load center.

1) Treat new load center as a sub-panel, an I believe that would mean I need to either install new grnd. bars attached to the enclosure or steal two of the four grnd. bars from the neutral/grnd bar configuration that exists?

YES


2) Treat the new load center as an (series) extension of the meter/main combo and find a bonding screw to bond the neutral, grnd. and enclosure?

NO

3) Can I/should I, run a #4 bare Cu wire through the nipple from the meter/main into the load center and what do I do with it (a four wire set-up)?

NO .. to the panel only .. use 4/0 SER from the Meter/disconnect

4) If the load center needs the neutral/grnd busses attached to the enclosure where might I find such a bonding screw (it looks to be about 1/4 inch fine thread hole in the buss bar with the hole in the enclosure not threaded, like the screw would be self-tapping)? This would presume the load center is to be treated as an extension of the service entrance.

NO do not bosnd the Nuetral bar to the Panel, the newer Siemans panels (P) series are all set up and ready to go

5) If the load center is to be treated as a sub-panel, am I correct that the ground bars need to be separate from the neutrals and attached to the enclosure?

YES

6) When is it necessary to actually isolate the ground wires with an insulator?

You do not isolate the Ground wires .... you isolate the Neutrals ....

7) Please provide any other questions and answers to other aspects of my proposed situation that I have missed.

Thank You for any/all input?

call a qualified Electrician to preform this task
 
I am closing this thread, in accordance with the Forum Rules.

This site is designed for:

  • Contractors
  • Electricians
  • Engineers
  • Inspectors
  • Instructors
  • Other electrically related individuals
* This NEC? Forum is for those in the electrical and related industries. Questions of a "How-To" nature by persons not involved in the electrical industry will be removed without notice.
If you feel this action to be in error, feel free to contact me via PM to explain.

A reminder to all members, if you see a questionable post, feel free to report it by clicking the
report-40b.png
button at the bottom left corner of the post.
 
Status
Not open for further replies.
Top