I don't follow this purported argument at all. The #1 to the 125A non-backed up panel is obviously a tap (and subject to 705.12(B)(2)(2)). But the 200A feeder from the Gateway to the Backup Panel is just a continuation of the 200A feeder from the meter main to the Gateway. 705.12(B)(2)(1)(b) allows the power source interconnection in the Gateway like that because of the 200A main breaker in the backed up loads panel.
Now if the Backuped Panel had no main breaker (not sure if that's possible because of 408 requirements, I didn't check), then 705.12(B)(2)(1)(a) would govern, and the required ampacity would be ~325A. This is definitely a situation where 705.12(B)(2)(1)(a) should overrule 310.15(B)(7)(3), and perhaps 310.15(B)(7)(3) should have some language in it to make that explicit.
It's arguably a tap because it's not protected from overload by the multiple sources that are capable of feeding it simultaneously. It meets the 240.21 definition in that respect. Further, it would seem that 705's language about taps requires you to consider the current from all sources when sizing the conductors to the backed up panel just the same as to the non-backed up panel. It doesn't seem like there's an important difference between those two feeders here.
Are you referring to the feeder from the 200A meter main to the Backup Gateway? Why wouldn't 310.15(B)(7) apply to that?
Cheers, Wayne
Sorry, I was unclear. What I meant was in regard to backfeeding calculations only. If your backfeeding circuit current per 705 were, say, 190A, it's not clear that you can apply 310.15(B)(7) 'backwards' and use 2/0 cu conductors. Where as if your calculated load is 190A then that's what 310.15(B)(7) is clearly meant to apply to.