bradler
Member
- Location
- Bellingham, WA, USA
I am trying to bid a new project upgrading a residential shop to a 200 amp service. The existing meter base panel combo has a 100amp disconnect and is to be replaced with a 200amp meter main disconnect with feed through lugs to the shop. There is currently a three conductor service going to a pump house and another three conductor service going to the shop building with neutrals and ground terminated on the same bar. The existing panel in the shop has the bonding jumper installed. Does this not create the danger that if this panel loses its ground/neutral since the branch circuits have un-separated grounds/neutrals, that all grounded surfaces in the shop will be energized?
Perhaps three conductor services are allowed here (outside of normal city limits/inspector I usually work with) but why was this not originally wired with four conductors? As the meter main combo will be the first point of disconnect should the neutral bond not be required to happen here with four conductors/separate neutral and ground going to the shop? As we will be installing new wire from the meter/panel already it would be easy to run four conductor feeders to the shop and the new panel will not be bonded.
My big dilemma is then what to do with the three conductor service to the well house. Upgrading this to a four conductor feeder and re working the panel could more than double my bid. The guy that I sub my excavation too wants nothing to do with trenching to the well house because its a mine field of water lines, cable, high voltage, and septic lines plus the run is over 200feet. Maybe the inspector will let me leave the 3 conductor service to the well house and just reconnect it to the new meter/main?
Perhaps three conductor services are allowed here (outside of normal city limits/inspector I usually work with) but why was this not originally wired with four conductors? As the meter main combo will be the first point of disconnect should the neutral bond not be required to happen here with four conductors/separate neutral and ground going to the shop? As we will be installing new wire from the meter/panel already it would be easy to run four conductor feeders to the shop and the new panel will not be bonded.
My big dilemma is then what to do with the three conductor service to the well house. Upgrading this to a four conductor feeder and re working the panel could more than double my bid. The guy that I sub my excavation too wants nothing to do with trenching to the well house because its a mine field of water lines, cable, high voltage, and septic lines plus the run is over 200feet. Maybe the inspector will let me leave the 3 conductor service to the well house and just reconnect it to the new meter/main?