Being a 208 single phase service I don't see any issue at all. You might kill the power lift the GEC and carefully bring on loads while measuring the voltages from L to N.
So what are your thoughts on the GEC? I had over 20 amps at one point, why does the current just not use the grounded conductor back to the transformer?