View attachment 20786
If I provide the ground at the wireway as shown, is it acceptable for the socket/meter to not be grounded?
Thanks. So then do I show a ground conductor from the meter to the wireway? (3 wires + ground)
120/240-1Ph
View attachment 20786
If I provide the ground at the wireway as shown, is it acceptable for the socket/meter to not be grounded?
Ah ok, so you include the EGC from the disconnects on down.
What would I do without this site I don't know.
They would be connected to the service neutrals in the disconnects.I believe you'd need EGCs from the wireway through the disconnects, otherwise how would the EGCs "from the disconnects on down" be connected to the grounding system?
Bonding each enclosure and adding an EGC just creates additional parallel paths for grounded conductor current.If you're installing the GEC at the wireway as shown, I believe you'd need EGCs from the wireway through the disconnects, otherwise how would the EGCs "from the disconnects on down" be connected to the grounding system?