infinity said:
I was thinking you said 'by mistake they ran a #6 to the CEE" that the CEE was rebar. According to table 250.66, typically for a service smaller than 200 amps the bonding jumper or GEC to the rebar CEE could be smaller than #4.

Gotcha / I understand.....Sorry, it was the way I worded that post. One would think after all these years I would have learned how to type. Thanks Trevor.
 
dcspector said:
Gotcha / I understand.....Sorry, it was the way I worded that post. One would think after all these years I would have learned how to type. Thanks Trevor.


No problem. I wasn't trying to high jack this thread, but i did have an inspector insist that I needed a #4 to the rebar on a 150 amp service.
 
infinity said:
No problem. I wasn't trying to high jack this thread, but i did have an inspector insist that I needed a #4 to the rebar on a 150 amp service.

Gotta watch them Inspectors. I have a loose cannon runnin around out there myself. He is killing me.
 
infinity said:
No problem. I wasn't trying to high jack this thread, but i did have an inspector insist that I needed a #4 to the rebar on a 150 amp service.
That's a common erroneous requirement, from what I've seen.
 
georgestolz said:
That's a common erroneous requirement, from what I've seen.

Well I can see why. 250.52(3) and 250.66(B) just mention a minimum of a #4 and not larger than a #4..........Where does it break or draw a line between 100 amp or 200 amp on CEE, or as GEC are based on SE size 250.66? CEE is a minimum #4 cu the way I read it.
 
Last edited:
dcspector said:
CEE is a minimum #4 cu the way I read it.


That's if you only use 20' of bare copper conductor to make a CEE. If you choose to simply attach to the rebar then the bonding jumper or GEC is sized according to 250.66. A typical 150 amp service with #1 or #1/0 copper service entrance conductors would only require a #6 bonding jumper or GEC to the rebar.
 
infinity said:
No problem. I wasn't trying to high jack this thread, but i did have an inspector insist that I needed a #4 to the rebar on a 150 amp service.

Perhaps he had 250.64(B) in mind. #4 and #6 are treated differently as far as protection. Just a WAG. :grin:
 
Psychojohn said:
How come the POCO would require the meter socket to be 4' to 6' off the ground, when an underground pedistal places the meter about 3' up.

John when it comes to something like power company meter heights I will not listen to anyones opinion.

I go right to the power companies Green book usually available to anyone on line and get a definite answer in writing.

Even what the power company employees will tell you is wrong many times.

Most power companies have preferred heights but have exceptions for things like meter stacks that may have a meters from 15" to 78" AFF.
 
see that is what is confusing me. We dont have "meter maids" anymore. Nstar switched to the digital meters so all they have now is a guy in a car driving around and he has a computer that picks up the readings so the person does not have to get out at every car. Kinda cool I think :grin:
 
dSilanskas said:
Nstar switched to the digital meters so all they have now is a guy in a car driving around

NStar Boston.....Requirments For Electric Service (PDF)

Right from Nstars own book

704. Meter Locations

A. Outdoor Meters
Outdoor meter sockets should be mounted so that the face of the meter is less than 6 feet above the final grade. In no instance will any meter be installed with the center of the meter more than 6 feet, nor the center of the meter less than 3 feet above the final grade. A clear area of 3 feet is required in front of each meter.(See Sketch 13)

Installation On Poles
NSTAR does not permit the installation of meters on its poles, except for cable TV amplifiers. Specific approval shall be obtained by NSTAR for such installations and shall conform to Massachusetts Electrical Code requirements. (Refer to Article 907)

Installation On Pedestal
For residential and small commercial applications only, the installation of the meter socket shall be permitted to be mounted on a free-standing pedestal pending the approval of the authority having jurisdiction. The customer may be required to provide protective devices for and at the free-standing pedestal. (See Sketch 14)

B. Indoor Meters
Multiple meter bank-installed indoors shall be mounted so that the center of the top meter(s) is no more than 6 feet and the center of the bottom meter is no less than 3 feet above the floor level. A clear area of 3 feet is required in front of each meter.
 
JohnJ0906 said:
Perhaps he had 250.64(B) in mind. #4 and #6 are treated differently as far as protection. Just a WAG. :grin:


Protection wasn't an issue. The #6 was run with and secured to the building surface.
 