LarryFine
Master Electrician Electric Contractor Richmond VA
- Location
- Henrico County, VA
- Occupation
- Electrical Contractor
The separate jumper for each disco presumes separate enclosures. You have a single assembly.Can anyone please help with post #18 questions? 250.24 allow either one overall MBJ for assembly or each service disco have its own MBJ but post #18 case has manufacturer provided two neutral bars and two EGC bars on ether side for 3 service disco either side one enclosed assembly.
Your PDF shows that the neutral and GECs land in the left side and EGCs land in the right side.
In any case, the entire assembly requires only single connections. Don't think about it as six separate disconnects.