Meter stack - separate enclosures

Lem

Member
Location
Minnesota
I am looking for some clarification on an existing meter stack for an apartment complex. The building has a 600 amp main service disconnect in its own enclosure feeding 12 meter sockets with individual disconnects. The customer wants to add 3 small apartments and I happen to have 3 empty meter sockets available. My question is regarding 230.71(B). If my main service disconnect is in its own enclosure, are the individual meters/disconnects required to have barriers as well? They currently do not have barriers.

Thank you.
 
No you do not.

Also, that 600A disco can be the service disconnect, or a “meter disconnect switch”, which, to my understanding, would not have the main bonding jumper installed in it.
 
Top