Buck Parrish
Senior Member
- Location
- NC & IN
I have used a 125amp meter base combo service panel. No Main
This panel I used to feed an existing 100 amp panel a 30 amp AC
And I installed two single pole 20's for wall outlets.
This panel's bus bar has 4 spaces, two spaces that you can not install half in. breaker. The other two spaces you are able to install 4, 1/2 in. breakers.
I used a 1 in. ea. 2 pole 100 amp , then four 1/2 in. ,togethet with the outside being the two pole 30 for the ac. The other two I used for two 1/2 in. single pole 20's, wall outlets.
I know that most panels with out a main you can not run the lighting or branch circuit out of it. But generally it will tell you on the panel cover.
Which I read and it said nothing about it.
I've not talked to the inspector but he left a message saying I could not use the 20's.
The way the panel is arranged you can turn every thing off with 6 motions.
And you can not put more spaces in it, It will only hold 2- 1 in. and either 2 more 1 in. or 4 -1/2 in. 6 total
My question is can I use it with 1 - 2 pole 100 amp breaker and four 1/2 in. one 2 pole 30 and two single pole 20's.
The inspector seems to be concerned with the 20's
This panel I used to feed an existing 100 amp panel a 30 amp AC
And I installed two single pole 20's for wall outlets.
This panel's bus bar has 4 spaces, two spaces that you can not install half in. breaker. The other two spaces you are able to install 4, 1/2 in. breakers.
I used a 1 in. ea. 2 pole 100 amp , then four 1/2 in. ,togethet with the outside being the two pole 30 for the ac. The other two I used for two 1/2 in. single pole 20's, wall outlets.
I know that most panels with out a main you can not run the lighting or branch circuit out of it. But generally it will tell you on the panel cover.
Which I read and it said nothing about it.
I've not talked to the inspector but he left a message saying I could not use the 20's.
The way the panel is arranged you can turn every thing off with 6 motions.
And you can not put more spaces in it, It will only hold 2- 1 in. and either 2 more 1 in. or 4 -1/2 in. 6 total
My question is can I use it with 1 - 2 pole 100 amp breaker and four 1/2 in. one 2 pole 30 and two single pole 20's.
The inspector seems to be concerned with the 20's