?*!whatthe?
Member
A strip mall with a 2000 amp, 120/208 volt, 3 phase exterior distribution panel contains a main circuit breaker as the service disconnect. Circuit Breakers will be added to this panel to feed power to the individual units as they are leased. Thirty feet away on both sides of this Panel are huge Gutters designed to feed the individual units of the mall. Six 4" PVC conduits run to each gutter from the service panel, all of which is for future use. At this point there is no metering of the service. Question: Does the NEC stipulate a maximum distance between the meter and the switch feeding it? Question: Since the bonding of the neutral is done at the panel, will the meters need to have Isolated neutrals in each?