Are theses instantaneous voltage drops due to associated loads? Or is this a steady state condition. Re: This is an instantaneous measurement performed by the meter on a corridor receptacle circuit in a school. No other loads are present on the circuit.
Is the VD only in the branch circuits, or is this from the Main Service to the utilization outlet? IE You measured voltage at the Main Service and there is a 15% drop to the furthest outlet? Re: From my understanding, the meter measures the no load voltage and then drops and instantaneous load onto the circuit and measures that voltage. It then calculates the delta V based on those values and divides that number by the no load voltage at the outlet. So, it is relative to the branch circuit voltage drop only.
Is the VD % you mentioned from a maximum (typical off hour measurement) to a minimum peak operating hours. Or is this a calculation you made using nominal 120 VAC. Re: This test/measurement was performed on a non-loaded 120V receptacle circuit.