What is the process of terminating MI cable? You can get it with the termination attached right? Thanks

Yes, if it is possible, the best way to order MI cable is with pre-made ends to the specific lengths. Some also add excess loop coiled up at one or both ends in case it needs to be repaired.

Field terminating MI cables is almost as tricky as old, taped MV cable terminators. The magnesium oxide compacted powder that provides the insulation between the conductors and the outer sheet is highly hygroscopic and the moisture trapped within eventually will result in the deterioration of the insulation value and to failure.
 

Alwayslearningelec

Senior Member
Location
NJ
Occupation
Estimator
Yes, if it is possible, the best way to order MI cable is with pre-made ends to the specific lengths. Some also add excess loop coiled up at one or both ends in case it needs to be repaired.

Field terminating MI cables is almost as tricky as old, taped MV cable terminators. The magnesium oxide compacted powder that provides the insulation between the conductors and the outer sheet is highly hygroscopic and the moisture trapped within eventually will result in the deterioration of the insulation value and to failure.

Thanks very much. I am little lost when you talk about the field terminations. Why exacty is it tougher? And if you order it with pre-made ends what is invloved in terminating to the equipment? Thanks.

Do you have a pic of a pre-made end? Thanks.
 

iwire

Moderator
Staff member
Location
Massachusetts
We do our own terminations and have not had any troubles. It would be a pain in the ass to use pre-made lengths.

Of course none of our MI work is above 480 volt or exposed to the elements. Perhaps that makes a difference.
 

Alwayslearningelec

Senior Member
Location
NJ
Occupation
Estimator
We do our own terminations and have not had any troubles. It would be a pain in the ass to use pre-made lengths.

Of course none of our MI work is above 480 volt or exposed to the elements. Perhaps that makes a difference.

Thanks IWIRE. So what is the process of an MI cable termination...if you don't mind? Thanks
 