MI Splice

Status
Not open for further replies.

Alwayslearningelec

Senior Member
Location
NJ
Occupation
Estimator
For larger size single conductor MI cable Anyone familiar with when you would or need to splice? Not when you transition to THHN when you make terminations More curious about in the middle of a run. Thanks
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
We use a stainless steel splice box with an individual connector for each phase and Hypress crimp barrel couplers. They get insulated with a cold shrink. We also cut slots between the connectors.
 