I have installation with (30) PV panels on the roof. This installation is under NEC 2014. Originaly there was going to be a String-Inverter installed but the client has opted for Micro-Inverters due to shading, avoiding the Rapid Shutdown requirement and some other things. This is the first installation I have done with Micro-Inverters and a few things are standing out at me.
There are (15) micro-inverters installed for the (30) panels (2 pv panels per micro-inverter) and they have been divided up into (3) strings. These (3) strings of micro-inverters have a maximum output current of 11 amps each and the trunk cable is #12. All (3) strings of trunk cable go to my combiner box on the roof and are then combined onto #8 THHN (33 amps max AC output current, 40 amp OCPD) that is piped down the side of the house to a AC fused disconnect on the ground (40 amp) and then into the house panel onto a 40 amp backfed breaker.
The questions I have are:
Do I need an OCPD in the combiner box (20 amp in-line fuses) on the #12 trunk cable before it is spliced onto the #8 THHN?
I thought all Fuses had to be readily accessible, can I put them in the combiner box on the roof? (I thought I read an exception at one time)
Should I bring the (3) sets of #12's down and put (3) 20 amp backfed breakers in the Panel (400 amp panel, will not violate 120% rule) or should I combine them in combiner box next to the disconnect on ground level with OCPD?
Thanks for any advise
There are (15) micro-inverters installed for the (30) panels (2 pv panels per micro-inverter) and they have been divided up into (3) strings. These (3) strings of micro-inverters have a maximum output current of 11 amps each and the trunk cable is #12. All (3) strings of trunk cable go to my combiner box on the roof and are then combined onto #8 THHN (33 amps max AC output current, 40 amp OCPD) that is piped down the side of the house to a AC fused disconnect on the ground (40 amp) and then into the house panel onto a 40 amp backfed breaker.
The questions I have are:
Do I need an OCPD in the combiner box (20 amp in-line fuses) on the #12 trunk cable before it is spliced onto the #8 THHN?
I thought all Fuses had to be readily accessible, can I put them in the combiner box on the roof? (I thought I read an exception at one time)
Should I bring the (3) sets of #12's down and put (3) 20 amp backfed breakers in the Panel (400 amp panel, will not violate 120% rule) or should I combine them in combiner box next to the disconnect on ground level with OCPD?
Thanks for any advise