Hendrix
- New England
How do inspectors deal with these? Where and how would you deal with the AC power coming streight off the aray?
I say "nice install, I don't know why more companies aren't using these" and I sign the card and get in my truck and go to the next job.
Can I come install in your jurisdiction?![]()
One thing I hope most inspectors would understand is that article 690 explicitly allows a connector (such as the one Enphase uses between its M215 and the trunk cable) to serve as an AC disconnect if it is listed for the purpose. Also, that the various requirements for DC PV source and output circuits should not apply to inverter output circuits for micro-inverters, even though the conduit coming from the roof may look the same. (Yes, you can run romex from micro-inverters, where it is appropriate to run romex, as long as you have the proper size DC GEC.)
I looked at one of these installations today using micro invertors. 240 volt AC had some concerns.
The conduit from the array has 5 sets of 10 AWG ungrounded, 5 -10 AWG N & Two 6 AWG grounds to a main lug distribution panel in the basement.
The panel is being used as a combiner for the array circuits. Five two pole 20 amp breakers back feed the distribution panel.
Two # 6 AWG Un-grounded conductors and One #10 AWG neutral and one # 6 ground back feed a 70 amp Two pole breaker in a 150 amp sub panel in the basement
The 6 AWG -10 AWG N- 6 AWG Grounds feed the utility required disconnect on the out- side of the single family dwelling from that disconnect they back feed ( 70 amp 2/pole breaker)the 150 amp sub- panel in the basement.
I asked some questions on this installation the contractor said no inspector ever questioned him on this in the past and he installed a hundred or so just like this. I?ll will give him the benefit of his specialized experience in this field; I will go back over article 690 and address my concerns
Not sure if I am understanding your question correctly but I don't think the 120% rule applies if your panelboard is being used as a combiner box that contains only backfed breakers and is line side connected to the incoming service. I would post this question in the PV forum.I looked at one of these installations today using micro invertors. 240 volt AC had some concerns.
You can use the breaker as the AC disconnect too. The seperate, lockable one is mostly required by the POCO's and the fire departments, that don't understand solar.
I did an inspection on a similar installation yesterday but did not pass it, because there was no dc connection to building ges. Also the egc could not qualify as a gec/egc because it was not of sufficient size and it was not continuous.
Do you agree with what I did? Comments always welcome.
The conduit from the array has 5 sets of 10 AWG ungrounded, ...
I don't believe that the micro inverters give you any exception for the 120% rule.
It's somewhat a matter of interpretation, although the code writers pretty clearly did not intend to allow 'AC combiners' to be excepted from the 120% rule. My opinion is that inspectors should give leeway if they feel sufficiently assured that the combiner will never get reconfigured to handle any loads.
For more on this, see:
http://forums.mikeholt.com/showthread.php?t=141357
http://forums.mikeholt.com/showthread.php?t=140547
http://www.iaei.org/magazine/2011/0...-utility-interactive-pv-inverter-connections/
http://solarprofessional.com/forums/forum/messageview.cfm?catid=3&threadid=749&enterthread=y