Micrologic MCB with LSIG settings

Status
Not open for further replies.

Isaiah

Senior Member
Location
Baton Rouge
Occupation
Electrical Inspector
I have a 200AT/250AF MCB Micrologic with LSIG protecting a 3Ph 3W 480V switchrack horizontal copper bus rated 200A and 42kAIC. Do any of ther LSIG settings need to be adjusted if I add a single motor load of 15hp @ approx 21FLC?
 
The instantaneous may need to be adjusted depending on what it is set to now to overcome inrush. Hopefully the settings were chosen for the full 200A potential load originally.
 