Microwave and dedicated receptacle
hhsting
Does kitchen microwave not microwave oven require dedicated receptacle or can the microwave receptacle be part of parallel receptacles branch circuit? Where in code?
Sent from my SM-G935U using Tapatalk
peter d
New England
Are you talking over the range or one sitting on the counter? It does not require a separate circuit if the microwave is fixed in place and isn't more than 50% of the branch circuit rating of 20 amps. Practically this means a microwave needs a separate circuit.
hhsting
Over the range like in dewelling unit kitchen. Where in code it says all that?
Sierrasparky
USA
Electrician ,contractor
You need also follow the mfg instructions. Most I have seen require a separate circuit.
A 1000w Micro has a input of about 1500w
Look at 220.23
Little Bill
Tennessee NEC:2017
If it's going over the stove/range then it needs a separate circuit. The code says for "hood" and since the MW is there it needs it. Also the MW has an exhaust fan built in.
Sierrasparky
USA
The issue really is the what the manufacture says and also if its rated over 50% of the branch circuit. How many code sections does one need to say " separate or dedicated circuit "
There is no way around it unless its a free standing unit.
Sierrasparky
USA
Need to have some type of hood over a range. If gas it needs to exhausted to the outside. Not a NEC thing but a Building code thing.
Why would one install a range and no hood or downdraft:?
Again if it is built in it needs a dedicated circuit. If on a shelf free standing then no.
infinity
New Jersey
Journeyman Electrician
Range hood/micro combo are typically cord and plug connected and therefore require an individual branch circuit.
(4) Range Hoods. Range hoods shall be permitted to be
cord-and-plug-connected with a flexible cord identified as
suitable for use on range hoods in the installation instruc-
tions of the appliance manufacturer, where all of the fol-
lowing conditions are met:
(1) The flexible cord is terminated with a grounding-type
attachment plug.
Exception: A listed range hood distinctly marked to iden-
tify it as protected by a system of double insulation, or its
equivalent, shall not be required to be terminated with a
grounding-type attachment plug.
(2) The length of the cord is not less than 450 mm (18 in.)
and not over 900 mm (36 in.).
(3) Receptacles are located to avoid physical damage to the
flexible cord.
(4) The receptacle is accessible.
(5) The receptacle is supplied by an individual branch
circuit.
Sierrasparky
USA
Yes , several code sections point to the same requirement.
Individual branch circuit.
OP has not been back, I bet he gets it.
curt swartz
Electrical Contractor - San Jose, CA
San Jose, CA
I still have no idea what the OP is calling a microwave. They stated its not an oven and its not a hood.