Migb when required

Status
Not open for further replies.

nickelec

Senior Member
Location
US
Where and when are migb ( metal insulated grounding bushings) required to be used. I have been trying to locate a section and can't seem to find the wording.
Ty in advance

Sent from my SM-G950U using Tapatalk
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
Where and when are migb ( metal insulated grounding bushings) required to be used. I have been trying to locate a section and can't seem to find the wording.
Ty in advance

Sent from my SM-G950U using Tapatalk

I don't think it is ever "required" in the way you might be thinking.

If I understand what a migb is, it is just a grounding bushing that includes the plastic wire protecting throat. Sometimes a grounding bushing is required by code, sometimes the plastic throat. If both are required at the same place a bushing that has both features would be handy.
 

jumper

Senior Member
There is a code reference for bonding both ends of a metallic pipe with a GEC in it and a pipe with a #4 or larger may require a bushing or insulated throat fitting, as was stated above, but there is no set rule requiring a "MIGB" that I know of.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Concentric KO's over 250 volts to ground are one of the few places where they are required.
 

nickelec

Senior Member
Location
US
The migb then I'm speaking of is a metal insulated bushing with a plastic throat and a lug for bonding

Sent from my SM-G950U using Tapatalk
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
That is an option to satisfy the rule, but I do not think that an MIGB is required per se, no? Other methods could be employed.

Did not look up exact rule, so I could easily be shooting myself in the foot here.:)

I don't think it is "required" but it is the most practical solution to the actual requirements.
 

Smart $

Esteemed Member
Location
Ohio
A metal bushing on the threaded end of RMC/IMC is permitted to forego an inside-the-enclosure locknut... provided an exterior locknut is used and wrench tight. In most cases, you cannot do this with the male threaded end of a connector of any wiring method. There is often not enough internal thread in the bushing to solidly bond the enclosure wall between the connector flange and bushing. The test is being able to make it up wrench tight and not be able to spin the connector with the wrench on either side afterward.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
That is an option to satisfy the rule, but I do not think that an MIGB is required per se, no? Other methods could be employed.

Did not look up exact rule, so I could easily be shooting myself in the foot here.:)

On concentric and eccentric KO's over 250 volts to ground it's the only game in town. You cannot use the other approved fittings bonding locknuts or bonding wedges with those KO's.
 