That small conductor rule doesn't apply to art 430, 440 or some other applications.What's the wiring method? #10 NM cable has a max breaker size of 30 amps.
Or am I missing something?
Ron
What can require NM to be larger in this situation is the fact it has to have it's ampacity determined from 60C column where most other conductors we use we can use the 75C ampacity column.
10 AWG @ 60C however does have max ampacity of 30 amps but overcurent protection for an art 440 application can be higher. The conductor is still protected from overloading by the motor overload protector.