In Mike's latest EC&M article he suggested that for a 320A load he should use 600kcmil conductors which would be adjusted to 380A, due to the number of current carrying conductors. These feeders can be installed on a 400A OCP device per 240.4(B).
1) If we have more than 3 current carrying conductors as shown per the *picture aren't we safe to assume you are running this 400A feed in parallel? If so why wouldn't you cut the wire size to two sets of 4/0 in parallel?
Or even 3/0 if run in 2 separate raceways which is often the case.
2)If this was a 480V 3phase service and a step down transformer is installed on the load side then we would not necessarily need a neutral. With no more than 3 current carrying conductors couldn't we use 500kcmil which is good for 380A acceptable per 240.4(B)?
3) What is the cut off for 240.4(B)? meaning breakers and fuses all jump from 350A to 400A. So if my conductors after adjustments come out to 360A could they still be protected by a 400A breaker? I have always, by safe practice increased the wire size or decreased the breaker size.
In existing situations can I tell a customer that their installation is up to code if their conductors are rated for 351 Amps after adjustments but installed on a 400A breaker? I do not know if this adjusted calculation is even possible using listed materials but just look at it as an extreme hypothetical installation. Am I misinterpreting 240.4(B)?
Please note that I do not advocate or suggest we use the minimum requirements. It is good to know what the minimum requirement is in the case of existing installations.
*California just adopted the 2005 NEC in January, so this is my base of reference. I recognize the article pertained to 2008 NEC.
*The picture I reference shows a cross section of a single conduit with three current carrying conductors on the left and a single conduit with 8 current carrying conductors (incl. 2 neutrals "grounded conductor") on the right.
1) If we have more than 3 current carrying conductors as shown per the *picture aren't we safe to assume you are running this 400A feed in parallel? If so why wouldn't you cut the wire size to two sets of 4/0 in parallel?
Or even 3/0 if run in 2 separate raceways which is often the case.
2)If this was a 480V 3phase service and a step down transformer is installed on the load side then we would not necessarily need a neutral. With no more than 3 current carrying conductors couldn't we use 500kcmil which is good for 380A acceptable per 240.4(B)?
3) What is the cut off for 240.4(B)? meaning breakers and fuses all jump from 350A to 400A. So if my conductors after adjustments come out to 360A could they still be protected by a 400A breaker? I have always, by safe practice increased the wire size or decreased the breaker size.
In existing situations can I tell a customer that their installation is up to code if their conductors are rated for 351 Amps after adjustments but installed on a 400A breaker? I do not know if this adjusted calculation is even possible using listed materials but just look at it as an extreme hypothetical installation. Am I misinterpreting 240.4(B)?
Please note that I do not advocate or suggest we use the minimum requirements. It is good to know what the minimum requirement is in the case of existing installations.
*California just adopted the 2005 NEC in January, so this is my base of reference. I recognize the article pertained to 2008 NEC.
*The picture I reference shows a cross section of a single conduit with three current carrying conductors on the left and a single conduit with 8 current carrying conductors (incl. 2 neutrals "grounded conductor") on the right.