Mike holts opin, dielectric union

Status
Not open for further replies.
this is relation to my other posts bonding water pipe, dielectric fittings http://forums.mikeholt.com/showthread.php?t=100806

Whats your opinion of mike holts comment, especially what i put in bold.

mike holt said:
One thing that MUST not be done is to install a bonding jumper around a gas meter. Gas meters almost always have a dielectric union on the custormer side of the meter. Metal gas pipes have a negative direct current voltage on them for corrosion protection. The reason why underground gas pipes are insulated is to conserve corrosion protection current and to concentrate the voltage gradient at the suface of the pipe so that it does the most good.

Similarly, plastic underground gas pipes have an insulated tracer wire. This wire also has a corrosion protection voltage on it.

In both cases of metallic pipes and tracer wires the ability to place and audio tone current over the metal needs to be possible so that gas lines can be located. A few months ago a gas company technician was having a devil of a time across the street from us because someone who had patched some metal gas pipeline with plastic pipe had NOT hooked up the tracer wires so that the connection was electrically sound and chemically durable.

Mike Cole, mc5w at earthlink dot net

Michael R.Cole September 5 2006, 10:13 am EDT
 
brother said:
Whats your opinion of mike holts comment, especially what i put in bold.

If you where to put a jumper around an intentionally installed die-electric union you would be defeating the purpose of the die-electric union.

But your post is confusing, where does Mike Holt's comment stop and Mike Cole's begin?
 
OT, It seems I remember this guy Mc5w owns stock in a silicone company?

Roger
 
There is a major difference in the function of the dielectric fitting in the gas piping as opposed to one used in water piping. The purpose of the one on the gas system is to prevent current on the underground gas piping that would defeat a cathodic protection system. The one on the water pipe is to prevent direct contact of two metals that will set up an electrolitic cell and cause corrosion.
 