beanland
Senior Member
- Location
- Vancouver, WA
Installed new Milbank 400A CL320 outdoor meter-main with two 200A Milbank labeled main breakers. We are having instantaneous trips at 400-500A; breaker magnetic element should not operate until 1200-2000A. Has anyone had similar problems?