Yes maximum size breaker 50 minimum ampacity 30.9. I would have used #10 before.
but I thought he could only use this wire for the given application (article 440) under 2 conditions:
1) 60 degree column works (it doesn't, he needs next size #8)
2) per 440 (or 430 per 440.7), the unit is marked and says on the label "max size breaker 50A" (he didn't say this but I am guessing everyone assumed it ?)
#10 would be fine if it were piped.Yes maximum size breaker 50 minimum ampacity 30.9. I would have used #10 before.
#10 would be fine if it were piped.
Scrape the .9 off of the tag.
So I'll use 8 to the disco. #10 to the unit.
All wire references are copper.
Unless you want to change to some other wiring method than NM.
I before E, except after C.Oh, Thanks cheif !
I before E, except after C.
Ask anyone who does crossword puzzles: names don't follow the rules of English.Oh yeah, I should have know. I went to school in Raleigh.
You mean #10 thwn yes?
Yes #10 thhn
Under 05 It would have been okay to use the 75 degree column , am I right ????
Yes #10 thhn
Under 05 It would have been okay to use the 75 degree column , am I right ????
With all the talk about the 60 degree coloum in 310.16. I am second guessing my self. Is #10 Romex okay on a 240 v Geothermal Heat Pump? The breaker will be 50 amps, the minimum circuit ampacity is 30.9.
Is romex #10-2 WG okay?