Min. cover requirements

Status
Not open for further replies.

olly

Senior Member
Location
Berthoud, Colorado
Occupation
Master Electrician
Can someone please confirm trench depth on 240V feeder direct buried on residential property through an open field. I see 18" in table 300.5 but I have a guy arguing with me that it should be 24"
 

Dzboyce

Senior Member
Location
Royal City, WA
Occupation
Washington 03 Electrician & plumber
If its an open field that is FARMED, we bury everything 5 feet deep. Its not uncommon to deep rip fields 3 feet deep.
 

Fred B

Senior Member
Location
Upstate, NY
Occupation
Electrician
Can someone please confirm trench depth on 240V feeder direct buried on residential property through an open field. I see 18" in table 300.5 but I have a guy arguing with me that it should be 24"
What year code cycle you looking at?
 

suemarkp

Senior Member
Location
Kent, WA
Occupation
Retired Engineer
How does 300.5 allow 18" for direct bury? I see 18" if under a residential driveway or parking area, but an open field is not that. Would think you need the 24" depth as specified in the first row and first column. I always thought it was 24" direct bury and 18" if in PVC for residential bury or 12" for 20A branch circuits that are GFCI protected.
 

Hv&Lv

Senior Member
Location
-
Occupation
Engineer/Technician
Maybe I’m missing something here.. I see 24”
C5D5FD93-0421-4280-A027-8403559112E0.jpg
One- and two-family dwelling driveways and outdoor parking areas, and used only for dwelling- related purposes

So is a field considered an outdoor parking area? If so the entire property can be considered a parking area.
 