Customer requesting a New 400 amp service. He has two CNC machines he got. I posted about the Phase Converter https://forums.mikeholt.com/threads/cnc-machine-in-rotary-phase-conveter.2577835/
So this is a Residents ,He I putting the cnc in the garage and want another 200 amp panel. His load is quite large. One is
Specs say 22.4kw that just for motor so used Full load at 70 gets me at 27.885 kw
His others is Full load of 40 amps at 230 volt 3/0 is 15.934 kw at power factor of 1. None of these state what power factor they are at how should I go with that.
These are 3/0 equipments. There going to be running for more than 3 hours so 1.25 for each of them puts one at
27.885kw x1.25 = 34.85625 kw
15.934kw x1.25=19.9175 kw
Does the Rotary phase converter care about the 1.25 percent???
Either way with the unit he has, I am past he Max KW for his unit if he wants to run them both at the same time.
His unit is a Ad/ADX60, and is a 30KVA unit
That my first question.
Next what do I account for power loss on the phase converter????? is it not an issue to include in my load calc??